2204 views|2 replies

2618

Posts

0

Resources
The OP
 

From traditional substation to smart substation [Copy link]

 

Author: Kallikuppa Sreenivasa

Focusing on green power, improving efficiency, and adopting smart grid technologies, utility companies are upgrading from traditional substations to digital substations.

Substations interconnect different voltage levels and form a critical link between transmission, distribution and consumption. Primary equipment such as power transformers, circuit breakers and disconnect switches located in the substation switchyard protect and manage the grid power supply. Auxiliary devices such as protection relays and terminal devices are usually located away from the switchyard in the control room panel to protect, control and monitor the primary devices.

Measuring electrical parameters in traditional substations

Conventional instrument transformers such as voltage transformers (PT) and current transformers (CT) measure the high voltage and current flowing through the primary device. Copper wires connect the analog output of the transformer to the auxiliary device, and the number of copper wires increases depending on the application.

Figure 1 shows that separate CTs and PTs for protection, control, and monitoring lead to installation and maintenance complexity due to the large amount of copper wires, and increase potential failures that lead to higher costs. In addition, the use of multiple transformers results in different primary current and voltage digital values within the device, limiting system performance and reliability.

查看详情

Figure 1: CT and PT wiring in a traditional substation using copper wires

Digital Substation

The digital substation is part of the secondary system and includes all protection, control, measurement, condition monitoring, recording and supervision systems related to the primary process.

Digital substations replace hundreds (sometimes thousands) of meters of copper wires between switchyards and intelligent electronic devices (IEDs) with a few fiber optic cables. Digital substations that use fiber optic cables for communication use conventional or non-conventional instrument transformers (NCITs) and merging units to digitize data related to the process parameters being measured. Using less copper makes digital substations simpler, more compact, and more efficient.

Digital Substation Architecture

According to the definition of the International Electrotechnical Commission (IEC) 61850 standard, the digital substation architecture includes three levels: process level, bracket level and station level, as shown in Figure 2.

查看详情

Figure 2: Digital substation architecture

Each level performs a specific function and the applications work together to implement the digital substation functions.

The process level includes power transformers, instrument transformers, and switchgear. The process level is the interface between primary and auxiliary (protection and control) components. In a traditional substation, the interface is hardwired with copper cabling; currents and voltages are passed to the protection and control panels at acceptable standardized auxiliary signal levels, while control cables send and receive status information. In a digital substation, all data - analog and binary - is digitized close to the source and sent to the IED over fiber optic cables using the IEC 61850-9-2 protocol.

The bay level includes auxiliary devices or IEDs such as bay controllers, protection relays, fault recorders, and meters. IEDs no longer have analog inputs because data acquisition occurs at the process level. Consolidated inputs can also reduce or eliminate the need for binary inputs, enabling compact devices that typically occupy only half the traditional footprint. IEDs handle protection and control algorithms and logic, make trip/no-trip decisions, and provide IEC 61850-based communication capabilities for lower (process) and upper (station) level Ethernet networks. Communication network redundancy is a typical requirement to ensure the highest availability and reliability. Two IEC 62439 standards - High Availability Seamless Redundancy (HSR) and Parallel Redundancy Protocol (PRP) - facilitate IED interoperability and integration from different vendors into substation networks.

The station level includes substation computers, Ethernet switches, and gateways. In addition to the traditional supervisory control and data acquisition (SCADA) bus, the substation bus provides additional communication capabilities because it allows multiple clients to exchange data; supports point-to-point device communication; and links to gateways for inter-substation and wide-area communication. Station-level devices may include substation human-machine interfaces (HMIs), engineering workstations accessed by IEDs or local centralization and archiving of power system data, SCADA gateways, proxy server links to remote HMIs, or controllers.

Measuring electrical parameters using merging units

The merging unit converts the instrument transformer output to a standardized Ethernet-based data output and implements IEC 61850.

In a digital substation, instead of connecting the sensor outputs to protection and control devices at the bay level, merging units are placed near the sensors that are connected to the master devices at the process level.

The merging unit converts analog signals (voltage, current) into sampled values based on IEC 61850-9-2 for protection, measurement and control, and communicates with the IEDs in the substation via digital communication, as shown in Figure 3. Some key merging unit functions include analog-to-digital conversion, resampling, synchronization with a global time base, sample conversion to IEC 61850-9-2 protocol, and communication with the IEDs using a fiber-optic Ethernet interface.

查看详情

Figure 3: Merging unit with conventional transformer

The merging unit performs the necessary processing to generate an accurate, time-aligned output data stream of sampled values in accordance with the IEC 61850-9-2 standard. This processing includes sampling of analog values; accurate real-time referencing; message formatting into sampled values; and publishing of a single data source to measurement, protection, and control devices.

查看详情

Key challenges in designing a merging unit

There are multiple challenges when designing a merge unit. Some of the key challenges that impact architecture and performance include:

  • Select an ADC that can scale the sampling rate and synchronize the sampling with a precise global timing reference.
  • Connect multiple ADCs to a host processor and capture data in real time to increase the number of analog input channels.
  • Capture sampling in real time to meet protection and measurement sampling requirements.
  • Communication using Ethernet with fiber optic interface
  • The communication protocol is implemented according to IEC 61850-9-2 and enables the sampled data to be communicated to multiple users without packet loss.
  • Enables the protocol stack to be used to implement redundancy protocols including HSR, PRP, and time synchronization based on the Institute of Electrical and Electronics Engineers (IEEE) 1588 Precision Time Protocol (PTP).
  • Implement multiple I/Os including binary inputs (16 or more inputs), cover wide AC and DC inputs and DC sensor inputs and outputs, and have expansion options.
  • Operate reliably in harsh switchyard environments with high transients, higher ambient temperatures and magnetic fields.

Solving Merge Cell Design Challenges

Integrated circuits and reference designs from Texas Instruments (TI) can help designers meet these challenges. Figure 4 shows the functional blocks in a merging unit.

查看详情

Figure 4: Merging unit block diagram

  • The merging unit consists of multiple subsystems described below that are interconnected to perform signal scaling/capture, processing, and communication functions. The unique features and capabilities (in brackets) of the TI recommended devices simplify the selection of key components and minimize the design effort.
  • The processor module (using AM3359 or AM4372 or AM5706 or AM6548) is connected to the ADC using the Programmable Real-Time Unit Industrial Communication Subsystem (PRU-ICSS) and includes a Digital Signal Processor (DSP) core for processing electrical parameters and algorithms and an Arm Cortex-A15 microprocessor subsystem for external communications, user interface, and execution of substation communication protocols.
  • The Ethernet interface (DP83822, DP83840) uses fiber optic cable or copper wire to connect to a host using the Media Independent Interface (MII) or simplified MII and hardware-assisted IEEE 1588 PTP-based time for communication synchronization at speeds of 100 Mbps.
  • AC/DC (Using UCC28600, UCC28740, UCC24630) wide input, high efficiency, synchronous rectifier based power supplies.
  • A DC/DC power tree (using LMZM33604, TPS82085) that includes high-efficiency power modules with small size, integrated inductor, and > 2-A load current, with fast transient response and reduced electromagnetic interference (EMI) due to integration of the controller, high-side and low-side FETs, and inductor in one package.
  • Memory termination (using TPS51200, TPS51116) using JEDEC-compliant source or sink double data rate (DDR) termination LDOs or an all-in-one DDR power management device with a synchronous buck controller, LDO, and buffered reference.
  • AC analog input modules (using OPA4188, THS4541, ADS8588S, ADS8688, AMC1306x) include AC voltage and current inputs for protection, monitoring, and measurement. Gain amplifiers scale the output of the sensor to the ADC input range. 16-, 18-, or 24-bit precision successive approximation registers or delta-sigma ADCs acquire samples at 80 or 256 (or higher) per cycle, synchronized to a global time reference using pulses per second or inter-range instrument clusters.
  • DC analog input or RTD module (ADS1248, ADS124S08) for bidirectional or unidirectional DC voltage or current control operation for remote communication between devices. 24-bit precision delta-sigma ADC improves measurement range and accuracy.
  • Binary input modules (ADS7957, ISO7741, ISOW7841) for monitoring batteries, providing interlocks between devices and indicating configuration changes and status. ADC and digital isolator-based architectures improve measurement accuracy and reduce circuit complexity by using fewer components compared to optocoupler- and Zener-diode-based designs.
  • Relay or high-speed type digital output module (using TPS7407, DRV8803) is used for alarm and external circuit breaker operation.
  • On-board protection of the analog inputs against transients (using TVS3300 or TVS3301) and board-level diagnostics (using HDC2010, TMP423, and TMP235) are used to measure ambient temperature/humidity for measurement drift compensation.

The merging unit connects to different types of transformers for measurement, including traditional instrument transformers, NCITs (such as optical current transformers), or Rogowski for current and resistor-capacitor voltage transformers (RCVTs) for voltage. NCITs connected to the merging unit, as shown in Figure 5, provide the option of metering, protection, and control accuracy in a single device. NCIT technology reduces transformer size and weight, saving space and cost.

查看详情

Figure 5: Merging unit connected to non-conventional instrument transformer

NCIT offers:

  • Improved measurement accuracy with wide dynamic range from sensor non-saturation effects.
  • Improved accuracy when measuring transients and harmonics.
  • Improved safety due to reduced risk of internal arcing and secondary open circuit faults.

in conclusion

The merging unit is a key component for utilities to move from traditional substations to digital substations. It simplifies the complexity of installation by reducing the number of copper wires and improves measurement accuracy because it is installed close to the main components. The merging unit can also be connected to the NCIT. NCIT is safer, smaller, more accurate, has a wider measurement range and is less expensive. The fiber optic communication interface improves the ability to resist interference present in the switchyard and minimizes communication failures.

Other merging unit benefits include extended life, improved reliability and availability of key components. TI's analog, power, interface, clock and embedded processor products, features and reference designs can help merging unit designers reduce effort and optimize costs.

This post is from TI Technology Forum

Latest reply

What is the cost of merging units?   Details Published on 2019-11-29 08:09
 

2w

Posts

341

Resources
2
 

What is the cost of merging units?

This post is from TI Technology Forum

Comments

I haven't really paid attention to the details of this, and it probably won't be cheap in the early stages, but it feels pretty smart.  Details Published on 2019-11-29 08:57
 
 
 

2618

Posts

0

Resources
3
 
qwqwqw2088 posted on 2019-11-29 08:09 What is the cost of merging units

I haven't really paid attention to the details of this, and it probably won't be cheap in the early stages, but it feels pretty smart.

This post is from TI Technology Forum
 
 
 

Guess Your Favourite
Find a datasheet?

EEWorld Datasheet Technical Support

EEWorld
subscription
account

EEWorld
service
account

Automotive
development
circle

Copyright © 2005-2024 EEWORLD.com.cn, Inc. All rights reserved 京B2-20211791 京ICP备10001474号-1 电信业务审批[2006]字第258号函 京公网安备 11010802033920号
快速回复 返回顶部 Return list