Communication between Yitong Chuanglian MODBUS to PROFIBUS gateway and Honeywell DCS system [Copy link]

Abstract: This article introduces how to use the MODBUS to PROFIBUS fieldbus gateway to achieve communication between Siemens S7-300PLC and Honeywell DCS system.

1. Composition and implementation method of communication system

Honeywell's DCS system communication uses MODBUS communication protocol, while Siemens PLC's data acquisition communication protocol for central air-conditioning chillers is Profibus-DP. In this system, Siemens PLC (S7-300) serves as the Profibus-DP master station, and the modbus to Profibus gateway YT-PB-01 serves as the Profibus-DP slave station. At the same time, the modbus to Profibus gateway YT-PB-01 executes the MODBUS RTU protocol through the RS485 interface and communicates with the Honeywell modbus master station host computer, so as to monitor and collect data on the temperature, water flow, pressure and other related parameters of the chillers of the central air-conditioning system of the Beijing Garden Museum.

1.1 System Configuration

SIEMENS's CPU315-2DP is used as a Profibus DP master station, and the bus address is set to 2; Yitong Chuanglian's modbus to Profibus gateway YT-PB-01 is used as a PROFIBUS-DP slave station, and the bus address is set to 3; the MODBUS slave station address is set to 1. The system connection diagram is shown in Figure 1:

Figure 1: System connection diagram

1.2. Parameter settings of modbus to Profibus gateway YT-PB-01

The YT-PB-01 modbus to Profibus gateway from Yitong Chuanglian can convert RS232 or RS485 protocol interfaces and supports Modbus RTU protocol. It can also be used as a master or slave of MODBUS. Here we choose Modbus RTU protocol, RS485 interface, and MODBUS slave mode.

The following is the corresponding configuration of the gateway:

1.3. Honeywell host computer MODBUS master station communication settings

Honeywell host computer MODBUS master station selects MODBUS protocol for communication. According to the configuration information already configured in the gateway, set the communication parameters as follows: slave address is 1; baud rate is set to 9600; 8 data bits; 1 stop bit; no parity; other parameters use default values. Please refer to the manual for related operations such as reading and writing data areas. According to the slave station data area settings, the address of the read temperature, pressure and other information should correspond to the address of the master station reading the main station. The MODBUS master station reads the slave station address parameter setting starting from 0.

1.4. PROFIBUS communication data settings

1.4.1. PROFIBUS communication data

1.4.2. Configuration and programming of PROFIBUS master

Open the STEP7 programming software and install the slave GSD file of the Modbus to Profibus gateway YT-PB-01 into STEP7, and then configure it through the GSD file, as shown in Figure 3:

Table 3: PROFIBUS communication data volume settings on PLC (Q address is configured according to actual situation)

After the configuration is completed, compile and save.

Program the analog and digital addresses detected by the PLC to MOVE. For example, if the PLC analog input address is AIW0, then just MOVE AIW0 to PIW256. The master station inquiry time is determined by the DCS host computer system. The gateway responds once for each inquiry from the host computer.

3. On-site pictures

In the future, gateways used to convert between different protocols will play an important role in automation systems. As a universal protocol gateway, the Modbus to Profibus gateway YT-PB-01 has been put into practical use in many projects at home and abroad.

This post is from Discrete Device
 
 

Just looking around
Find a datasheet?

EEWorld Datasheet Technical Support

Related articles more>>
Featured Posts
[Classic Books] Bluetooth Core Technology (for reference by researchers and developers in the communications industry)

This book was written by two members who participated in the formulation of the Bluetooth standard. It consists of four ...

3G video service market survey and analysis (Yuan Xiaoming and Xue Yulin, School of Economics and Management, Nanjing University of Posts and Telecommunications)

In order to truly understand the consumer demand for 3G mobile video services, the author conducted a market survey on t ...

Software simulation of asynchronous communication of BF561 SPORT port

In various DSP application systems, the universal asynchronous receiver /transmitter (UART) is a commonly used communic ...

Inductor knowledge points record

This post was last edited by Xiao Wei Gege on 2021-10-9 09:52 1. Inductors are often used in switching power supply cir ...

【i.MX6ULL】Driver Development 7——Key Input Capture

This post was last edited by DDZZ669 on 2021-11-9 00:04 In the previous articles, we have gradually learned about the ...

[HPM-DIY]littlevgl benchmark score? Xianji hpm6750 or STM32h747 winer?

This post was last edited by RCSN on 2022-8-6 15:55 There is no need for comparative data, but out of curiosity, I wil ...

40 "Millions" of Raspberry Pi Cars - ROS Learning (C Language Programming to Control the Turtle)

This post was last edited by lb8820265 on 2022-11-1 14:52 In the previous section, we introduced how to run the "tu ...

Communication Cat MQTT server online client problem

I'm looking for a MQTT server online client on the Internet. I'm a little confused whether it is a server or a client. 6 ...

Evaluation shortlist: Sipeed BL808 all-round board, RISC-V triple-core, wireless triple-mode, AIoT+Linux+RTOS

Thanks to the netizens who participated in the Sipeed BL808 all-round board, RISC-V triple-core, wireless triple-mode, A ...

Looking for someone to try a USB packet capture tool, with compensation

Hello everyone, I have developed a USB packet capture tool and would like to find someone to try this product and see if ...

Copyright © 2005-2024 EEWORLD.com.cn, Inc. All rights reserved 京B2-20211791 京ICP备10001474号-1 电信业务审批[2006]字第258号函 京公网安备 11010802033920号
快速回复 返回顶部 Return list