1738 views|9 replies

442

Posts

2

Resources
The OP
 

What factors restrict the number of receiving terminals in the 485 communication mode of 1 send and 32 receive? Is it the distributed capacitance? [Copy link]

I would like to ask what factors limit the number of receiving ends in the 485 communication mode of 1 send and 32 receive? Is it the influence of distributed capacitance on the waveform?

This post is from PCB Design

Latest reply

[attach]433316[/attach] [attach]433317[/attach] [attach]433318[/attach] [attach]433319[/attach] [attach]433320[/attach] These are some reference materials I collected from TI's official website. You can also study and discuss together.   Details Published on 2019-9-17 13:40
 

2w

Posts

341

Resources
2
 

485 communication 1 send 32 receive belongs to differential mode,

Multiple nodes require terminal matching

This post is from PCB Design
 
 

1w

Posts

142

Resources
3
 

It is determined by the input impedance of the receiver. You can understand this by looking at the device manual of the 485 interface chip with more than 32 nodes.

This post is from PCB Design
Personal signature上传了一些书籍资料,也许有你想要的:http://download.eeworld.com.cn/user/chunyang
 
 
 

1048

Posts

1

Resources
4
 

The most critical parameter is the UL value (unit load) of the 485 chip, which is the input impedance (12Kohm) mentioned above. The 485 bus standard is to drive 32 ULs. If the selected 485 chip is 1/4UL, then the upper limit of the number of devices that can be driven by one bus is 32x4=128.

Secondly, it is related to the bias resistance value designed in your actual circuit, the bias pull-up voltage, and whether the terminal matching resistance is connected (so it is also related to the baud rate and distance. If the baud rate is low and the distance is short, there is no need to add terminal matching resistance).

This post is from PCB Design
 
 
 

442

Posts

2

Resources
5
 
topwon posted on 2019-9-16 16:44 The most critical parameter is the UL value (unit load) of the 485 chip, which is the input impedance (12Kohm) mentioned above. The 485 bus standard is to drive 32...
Thank you very much, but I still want to ask, if the receiver is a quarter of the UL, then it is 12K ohms/4=3K ohms, then the current on the 485 line will increase by 4 times, and the current of each of the 128 terminals will increase by 4 times, so the total current will increase by 128*4 times, which is incredible. Am I understanding it wrong?
This post is from PCB Design
 
 
 

1048

Posts

1

Resources
6
 
EEW2018 posted on 2019-9-17 07:35 Thank you very much, but I still want to ask, if the receiver is a quarter of UL, then it is 12K ohms/4=3K ohms, then the current on the 485 line will definitely increase by 4 times, so 12 ...

The input impedance corresponding to one quarter of UL is 12Kx4=48K ohms. . . . .

This post is from PCB Design
 
 
 

442

Posts

2

Resources
7
 
topwon posted on 2019-9-17 11:14 The input impedance corresponding to one-quarter UL is 12Kx4=48K ohms. . . . . .

Thank you very much. How to add matching impedance at the end of the line, how to calculate the value of matching impedance, and are there any construction pictures of adding matching impedance? Thank you.

This post is from PCB Design
 
 
 

1048

Posts

1

Resources
8
 
EEW2018 posted on 2019-9-17 11:39 Thank you very much. How to add matching impedance at the end of the line, how to calculate the value of matching impedance, and are there any construction pictures of adding matching impedance, thank you...

If the comparison between the cable length and the baud rate results in the need to consider it as a transmission line,

The simplest termination method is to connect matching resistors in parallel at both ends of the cable (if it is a unidirectional 485 network, then just on the far end). The value of the matching resistor should be consistent with the characteristic impedance of the cable used (485 cable is generally designed according to 120 ohm characteristic impedance).

It is important to remember that even if you need to add matching resistors, you can only add them at both ends of the entire cable and not at other nodes.

This post is from PCB Design
 
 
 

1048

Posts

1

Resources
9
 

RS-422-RS-485-eBook.pdf (5.02 MB, downloads: 7)

If you are interested, you can study this application document carefully. When is termination required, how to terminate, how to bias, etc.

This post is from PCB Design
 
 
 

1048

Posts

1

Resources
10
 

RS-485 basics - The RS-485 Driver.docx (68.61 KB, downloads: 0)



RS-485 basics - how to calculate unit loads and the maximum number of nodes on y.docx (101.51 KB, downloads: 1)

RS-485 basics - the RS-485 receiver.docx (155.54 KB, downloads: 0)

RS-485 basics - two ways to fail-safe bias your network.docx (62.87 KB, downloads: 0)

RS-485 basics - When termination is necessary, and how to do it properly.docx (105.62 KB, downloads: 0)

These are some reference materials I collected from TI's official website. You can also study and discuss together.

This post is from PCB Design
 
 
 

Find a datasheet?

EEWorld Datasheet Technical Support

EEWorld
subscription
account

EEWorld
service
account

Automotive
development
circle

Copyright © 2005-2024 EEWORLD.com.cn, Inc. All rights reserved 京B2-20211791 京ICP备10001474号-1 电信业务审批[2006]字第258号函 京公网安备 11010802033920号
快速回复 返回顶部 Return list